Hi Martin an Derek,
I just noticed that my steel trowels rust very(!) quickly if the user
forgets to wipe of the earth plaster right after use.
André, whipe'm clean, de Bouter
Le 25/08/2013 02:57, martin hammer a écrit :
> Re: [GSBN] Steel mesh in clay plaster (?) Hi Derek,
>
> A very thorough and thoughtful response, as always. Thank you.
>
> Thoughts and information are welcome from others as well.
>
> Martin
>
>
> On 8/24/13 5:51 PM, "Derek Roff" <derek at unm.edu> wrote:
>
> Hi, Martin,
>
> I will start with a quote from the site
> http://www.cement.org/tech/cct_dur_corrosion.asp: "Corrosion of
> reinforcing steel and other embedded metals is the leading cause
> of deterioration in concrete." This page is a fairly concise, not
> too technical description of reinforcing steel corrosion in
> concrete. The article points out that concrete contains all the
> ingredients necessary to cause corrosion in steel. Concrete
> itself can function as an electrolyte, and different locations in
> reinforcing steel can act as anode and cathode for inducing
> corrosion. The electrical conductivity of concrete is sufficient
> to support corrosion. If other metals, such as aluminum or zinc
> (galvanized metal) are in contact with the concrete, this
> increases the rate of corrosion for the reinforcing steel. On the
> other hand, in the galvanized metal itself, the zinc is a
> sacrificial layer, which protects the steel, for as long as the
> zinc lasts.
>
> Concrete also contains one significant corrosion inhibitor- high
> pH, which helps protect the steel, by aiding the formation of a
> thin, passivating protective layer on the surface of the steel.
> The author says that the "corrosion rate [of steel with the
> passive film protective layer] is typically 0.1 µm per year.
> Without the passive film, the steel would corrode at rates at
> least 1,000 times higher [100 µm per year] (ACI222 2001)." [If
> your mail program isn't showing the special characters properly,
> the measurement units are micro-meters per year, one millionth of
> a meter.] Lime also has a similarly high pH.
>
> The main causes of increased corrosion are salts in or applied to
> the concrete, and decreased pH. Salts may be common in the
> materials used as aggregate, in the water used for the mix, or may
> be introduced after the concrete has solidified. People add salts
> to concrete for ice removal and other reasons, and salts may also
> be introduced unintentionally by wind and water, in some locations.
>
> Decrease in pH can be the result of carbonation in the concrete,
> or acids in the environment, both naturally occurring and applied
> intentionally. Carbon Dioxide in the air reacts with water vapor
> to produce carbonic acid, so a small acid source is always
> present. Acid rain can introduce much stronger acids in greater
> quantities. Carbonation is usually slow for good, thick concrete
> made with pure materials, but may occur much more quickly in less
> pure concrete mixes and thinner applications, such as plasters.
> Carbonation is more rapid in lime mixes than in concrete. Cracks
> in the concrete or lime, of course, increase the rate of corrosion.
>
> Clays are highly variable, but are unlikely to have the high pH
> that helps form a protective layer on reinforcing steel in
> concrete and lime. I found a statement that natural clays can
> vary between pH 2 and 10. Within the pH range that is common for
> clays, neutral to slightly basic mixes will have the lowest
> corrosion rates, according to the websites that I checked. On the
> other hand, many clays will not act as an electrolyte. If an
> electrolyte is lacking, the rate of corrosion will stay low. This
> site http://www.ncbi.nlm.nih.gov/pubmed/22200075 contains an
> abstract on the use of clays "to impart remarkable protection
> against corrosion to galvanized steel." Salts may or may not be
> present in the clay, depending on the local conditions, water,
> geology, and the clay mix. Clay is a much better buffer for
> moisture than concrete is, which would usually help steel in clay
> resist corrosion. Clays are not subject to carbonation. Lower
> temperatures will reduce the rate of corrosion.
>
> The PDF freely downloadable at this site
> http://bookshop.europa.eu/en/corrosion-of-low-carbon-steel-in-clay-and-sea-sediments-pbCDNA10522/
> contains several interesting quotes, which are somewhat divergent
> from each other, and not identical to the conditions of
> reinforcing steel in clay plasters. The authors were concerned
> about steel immersed at high temperatures (90 degrees C) in sea
> sediments. While other sites have suggested that more water
> increases the rates of corrosion, this article finds the reverse,
> which they attribute to the lack of dissolved oxygen in the
> sediment zone they investigated.
>
> With no mention of the amount of water involved in the referenced
> studies, the authors say, "In literature, data can be found on
> corrosion of mild steel in clay. Exposing ductile iron or carbon
> steel [H. Tas SCK/CEN Mol, Personal communication] directly to
> clay at room temperature gives rise to general corrosion rates
> ranging from 10 to 50 µm/yr."
>
> However, their tests and references show a much lower corrosion
> rate of only 8 µm/yr in one study with steel in clay under
> unspecified conditions, and from another study, 2-10 µm/yr at
> 25°C, in bentonite clay.
>
> "Tests in deaerated substitute seawater were conducted at Harwell
> at 90°C [G.P. Marsh et al. - Corrosion assessment of metal
> operpacks for radioactive waste disposal - European Appi. Res.
> Rept. - Nucí. Sc. Technol., vol. 5, pp. 223-52 (1983)] which give,
> after a stabilization period of about 2.000 h a corrosion rate of
> about 8 µm/yr. Another series of tests was performed in which low
> carbon steel sample were embedded in bentonite saturated with a
> basic synthetic granite groundwater at 90, 50°C and at room
> temperature [K.J. Taylor, I.D. Blaid, C.C. Naish, G.P. Marsh -
> Corrosion stu dies on Containment Materials for vitrified Heat
> Generating Nuclear waste AERE G - 3217 (1984)]. After a
> stabilization period a corrosion rate ranging between 20-37 µm/yr
> at 90, 9-32 µm/yr at 50 and 2-10 µm/yr at 25°C was apparent."
>
> Based on the references that I could find, the rate of corrosion
> for steel in clay is substantially less variable than for steel in
> concrete. (I can't think of another example where a property of
> clay is less variable than an industrial product.) Steel deeply
> imbedded in excellent concrete, and protected by a passivating
> layer, will have a corrosion rate that is a tenth or less of that
> for steel in clay, according to the figures that I found. Steel
> imbedded in an average Portland cement plaster with some cracks,
> in which the passivating layer is absent or compromised, might
> have a corrosion rate fifty times higher than steel in a clay
> plaster.
>
> As with so many things in building, since testing reveals such a
> range of potential variability, it would be useful to test the
> materials under local conditions.
>
> I hope this is of some help.
>
> Derek
>
> On Aug 24, 2013, at 4:39 PM, martin hammer wrote:
>
> Steel mesh in clay plaster (?)
> Hello all,
>
> Can anyone weigh in on the use of steel mesh in clay plaster,
> in terms of corrosion of the steel? In particular if it is
> susceptible to a higher rate of corrosion than steel mesh in
> lime or cement plaster (or what an expected service life might
> be). Laboratory tested evidence is especially welcome, but so
> is anecdotal evidence (pro or con).
>
> I know there has been concern expressed about this for many
> years. I've heard theory, but I haven't seen hard evidence
> that it is actually a problem.
>
> I ask this in the context of a Strawbale Tutorial I am
> co-authoring for the World Housing Encyclopedia. The tutorial
> is meant as guide for constructing small houses in seismically
> active regions of the developing world. Thus the desire for a
> reinforced clay plaster as the in-plane lateral resisting
> system. Darcey Donovan has used nylon fishing net in her
> system with PAKSBAB in Pakistan (which was shake table tested)
> but I am looking to use other mesh materials where such
> fishing net might not be available. Metal mesh seems to be
> readily available in most of the developing world. (We are
> also considering natural fiber mesh, but these may have
> strength and degradation problems).
>
> Thanks!
>
> Martin
>
> PS -- I've copied my colleague, Dmitry Ozeryansky, PE
> _______________________________________________
> GSBN mailing list
> GSBN at sustainablesources.com
> http://sustainablesources.com/mailman/listinfo.cgi/GSBN
>
>
> Derek Roff
> derek at unm.edu
>
>
>
> ------------------------------------------------------------------------
> _______________________________________________
> GSBN mailing list
> GSBN at sustainablesources.com
> http://sustainablesources.com/mailman/listinfo.cgi/GSBN
>
>
>
> _______________________________________________
> GSBN mailing list
> GSBN at sustainablesources.com
> http://sustainablesources.com/mailman/listinfo.cgi/GSBN
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.sustainablesources.com/pipermail/gsbn/attachments/20130825/94777f0f/attachment.htm>
More information about the GSBN
mailing list