Classic Derek--thank you; I will keep this incredibly informative response on file. 

Here's our (short term this far; 5 years±) anecdotal experience with metal and clay, followed by a preview of where we're going with this. 

~~~~~~~~~~~~~~

We have every possible permutation and combination of clay and steel under testing in dry (20" rain)  so cal:

Cob, straw clay, heavy straw clay, earth plaster, lime plaster, aliz--

in contact with:

6-6-10-10 welded wire mesh, rebar and structural steel, all plain, unprotected-
plus heavy and light stainless steel meshes, various guages of galvanized mesh and lath, and painted structural steel. 

So far what I've observed is a high degree of initial corrosion in unprotected interior mesh caused by the sopping wet fresh mix, followed by...nothing much. 

I suspect that in this climate  that all this stuff is going to last for decades. Until something fails I'm not going to have much more to say about longevity.

By far the most charmed combination for structural strength and ease of construction among those that we've tried is 6-6-10-10 (6x6" squares, 10 guage) reinforcing mesh in cob. The configuration I'm most excited about is one in which there is a reinforcing layer just under both the inside and the outside surface of a classic compound curved, tapered wall cob building, with an integral cob floor and heavy straw clay ceiling.

Where corrosion concern, the reinforcing could be galvanized, painted or slathered with local organic beach tar. 

Structurally, this would be both a monolithic fibercomposite, and a stress-skin structure. It is also suited for a base isolation footing. There could be zero cement in the structure in this case.

The wrap-around several inches of earth would provide naturally extreme fire resistance. This would be coupled with fire safety details we've been working on, including metal framed cob doors and rooftop turbine ventilators. The idea here is to make a building that is without question more safe than a conventional building for structural and wildfire, with more than the required seismic safety. The initial application could be charming backyard cob playhouse/ impregnable fire bunkers, something that could be life-saving in this area.

Misha and I plan to pursue seismic testing of such a structural system next fall, along with our best shot at an organic-only reinforced structure (bamboo, rope, jute...?) If anyone has suggestions about reinforcing or anything else please charm in. I feel like we're way more on top of the steel reinforcement than the organic reinforcement scenario (awaiting direction from Massey on this).

Here's a slide show of our scale model testing. The steel model totally rocked this test--the equivalent of taking 2.4 g's of lateral, though at 12:1 there's plenty of error in the way it scales, this is encouraging. The orgainic-only model also did well--0.2 g's if memory serves, which used to be enough for California's old seismic standard and is also very encouraging for a first try.

Yours, 

Art

 (Note: There's also bunch of ferrocement in more exposed locations; it seems to play well with cob and ferrocob).

Quoting martin hammer <mfhammer at pacbell.net>:

> Hi Derek,
>
> A very thorough and thoughtful response, as always.  Thank you.
>
> Thoughts and information are welcome from others as well.
>
> Martin
>
>
> On 8/24/13 5:51 PM, "Derek Roff" <derek at unm.edu> wrote:
>
>> Hi, Martin,
>>
>> I will start with a quote from the site
>> http://www.cement.org/tech/cct_dur_corrosion.asp:  "Corrosion of reinforcing
>> steel and other embedded metals is the leading cause of deterioration in
>> concrete."  This page is a fairly concise, not too technical description of
>> reinforcing steel corrosion in concrete.  The article points out 
>> that concrete
>> contains all the ingredients necessary to cause corrosion in steel.  
>> Concrete
>> itself can function as an electrolyte, and different locations in 
>> reinforcing
>> steel can act as anode and cathode for inducing corrosion.  The electrical
>> conductivity of concrete is sufficient to support corrosion.  If 
>> other metals,
>> such as aluminum or zinc (galvanized metal) are in contact with the 
>> concrete,
>> this increases the rate of corrosion for the reinforcing steel.  On 
>> the other
>> hand, in the galvanized metal itself, the zinc is a sacrificial layer, which
>> protects the steel, for as long as the zinc lasts.
>>
>> Concrete also contains one significant corrosion inhibitor- high pH, which
>> helps protect the steel, by aiding the formation of a thin, passivating
>> protective layer on the surface of the steel.  The author says that the
>> "corrosion rate [of steel with the passive film protective layer] is 
>> typically
>> 0.1 µm per year. Without the passive film, the steel would corrode 
>> at rates at
>> least 1,000 times higher [100 µm per year] (ACI222 2001)."  [If your mail
>> program isn't showing the special characters properly, the measurement units
>> are micro-meters per year, one millionth of a meter.]  Lime also has a
>> similarly high pH.
>>
>> The main causes of increased corrosion are salts in or applied to the
>> concrete, and decreased pH.  Salts may be common in the materials used as
>> aggregate, in the water used for the mix, or may be introduced after the
>> concrete has solidified.  People add salts to concrete for ice removal and
>> other reasons, and salts may also be introduced unintentionally by wind and
>> water, in some locations.
>>
>> Decrease in pH can be the result of carbonation in the concrete, or acids in
>> the environment, both naturally occurring and applied intentionally.  Carbon
>> Dioxide in the air reacts with water vapor to produce carbonic acid, so a
>> small acid source is always present.  Acid rain can introduce much stronger
>> acids in greater quantities.  Carbonation is usually slow for good, thick
>> concrete made with pure materials, but may occur much more quickly in less
>> pure concrete mixes and thinner applications, such as plasters.  Carbonation
>> is more rapid in lime mixes than in concrete.  Cracks in the 
>> concrete or lime,
>> of course, increase the rate of corrosion.
>>
>> Clays are highly variable, but are unlikely to have the high pH that helps
>> form a protective layer on reinforcing steel in concrete and lime.  
>> I found a
>> statement that natural clays can vary between pH 2 and 10.  Within the pH
>> range that is common for clays, neutral to slightly basic mixes will 
>> have the
>> lowest corrosion rates, according to the websites that I checked.  On the
>> other hand, many clays will not act as an electrolyte.  If an electrolyte is
>> lacking, the rate of corrosion will stay low.  This site
>> http://www.ncbi.nlm.nih.gov/pubmed/22200075 contains an abstract on 
>> the use of
>> clays "to impart remarkable protection against corrosion to 
>> galvanized steel."
>> Salts may or may not be present in the clay, depending on the local
>> conditions, water, geology, and the clay mix.  Clay is a much better buffer
>> for moisture than concrete is, which would usually help steel in clay resist
>> corrosion.  Clays are not subject to carbonation.  Lower temperatures will
>> reduce the rate of corrosion.
>>
>> The PDF freely downloadable at this site
>> http://bookshop.europa.eu/en/corrosion-of-low-carbon-steel-in-clay-and-sea-sed
>> iments-pbCDNA10522/ contains several interesting quotes, which are somewhat
>> divergent from each other, and not identical to the conditions of 
>> reinforcing
>> steel in clay plasters.  The authors were concerned about steel immersed at
>> high temperatures (90 degrees C) in sea sediments.  While other sites have
>> suggested that more water increases the rates of corrosion, this 
>> article finds
>> the reverse, which they attribute to the lack of dissolved oxygen in the
>> sediment zone they investigated.
>>
>> With no mention of the amount of water involved in the referenced 
>> studies, the
>> authors say, "In literature, data can be found on corrosion of mild steel in
>> clay. Exposing ductile iron or carbon steel [H. Tas SCK/CEN Mol, Personal
>> communication] directly to clay at room temperature gives rise to general
>> corrosion rates ranging from 10 to 50 µm/yr."
>>
>> However, their tests and references show a much lower corrosion rate 
>> of only 8
>> µm/yr in one study with steel in clay under unspecified conditions, and from
>> another study, 2-10 µm/yr at 25°C, in bentonite clay.
>>
>> "Tests in deaerated substitute seawater were conducted at Harwell at 90°C
>> [G.P. Marsh et al. - Corrosion assessment of metal operpacks for radioactive
>> waste disposal - European Appi. Res. Rept. - Nucí. Sc. Technol., vol. 5, pp.
>> 223-52 (1983)] which give, after a stabilization period of about 2.000 h a
>> corrosion rate of about 8 µm/yr. Another series of tests was per­formed in
>> which low carbon steel sample were embedded in bentonite saturated with a
>> basic synthetic granite groundwater at 90, 50°C and at room 
>> temperature [K.J.
>> Taylor, I.D. Blaid, C.C. Naish, G.P. Marsh - Corrosion stu­ dies on
>> Containment Materials for vitrified Heat Generating Nu­clear waste AERE G -
>> 3217 (1984)]. After a stabilization period a corrosion rate ranging between
>> 20-37 µm/yr at 90, 9-32 µm/yr at 50 and 2-10 µm/yr at 25°C was apparent."
>>
>> Based on the references that I could find, the rate of corrosion for 
>> steel in
>> clay is substantially less variable than for steel in concrete.  (I can't
>> think of another example where a property of clay is less variable than an
>> industrial product.)  Steel deeply imbedded in excellent concrete, and
>> protected by a passivating layer, will have a corrosion rate that is a tenth
>> or less of that for steel in clay, according to the figures that I found.
>> Steel imbedded in an average Portland cement plaster with some cracks, in
>> which the passivating layer is absent or compromised, might have a corrosion
>> rate fifty times higher than steel in a clay plaster.
>>
>> As with so many things in building, since testing reveals such a range of
>> potential variability, it would be useful to test the materials under local
>> conditions.
>>
>> I hope this is of some help.
>>
>> Derek
>>
>> On Aug 24, 2013, at 4:39 PM, martin hammer wrote:
>>
>>> Steel mesh in clay plaster (?)
>>> Hello all,
>>>
>>> Can anyone weigh in on the use of steel mesh in clay plaster, in terms of
>>> corrosion of the steel?  In particular if it is susceptible to a 
>>> higher rate
>>> of corrosion than steel mesh in lime or cement plaster (or what an expected
>>> service life might be).  Laboratory tested evidence is especially welcome,
>>> but so is anecdotal evidence (pro or con).
>>>
>>> I know there has been concern expressed about this for many years.  I?ve
>>> heard theory, but I haven?t seen hard evidence that it is actually 
>>> a problem.
>>>
>>> I ask this in the context of a Strawbale Tutorial I am co-authoring for the
>>> World Housing Encyclopedia.  The tutorial is meant as guide for 
>>> constructing
>>> small houses in seismically active regions of the developing world. 
>>>  Thus the
>>> desire for a reinforced clay plaster as the in-plane lateral resisting
>>> system.  Darcey Donovan has used nylon fishing net in her system 
>>> with PAKSBAB
>>> in Pakistan (which was shake table tested) but I am looking to use 
>>> other mesh
>>> materials where such fishing net might not be available.  Metal 
>>> mesh seems to
>>> be readily available in most of the developing world. (We are also
>>> considering natural fiber mesh, but these may have strength and degradation
>>> problems).
>>>
>>> Thanks!
>>>
>>> Martin
>>>
>>> PS ? I?ve copied my colleague, Dmitry Ozeryansky, PE
>>> _______________________________________________
>>> GSBN mailing list
>>> GSBN at sustainablesources.com
>>> http://sustainablesources.com/mailman/listinfo.cgi/GSBN
>>
>> Derek Roff
>> derek at unm.edu
>>
>>
>>
>>
>> _______________________________________________
>> GSBN mailing list
>> GSBN at sustainablesources.com
>> http://sustainablesources.com/mailman/listinfo.cgi/GSBN
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.sustainablesources.com/pipermail/gsbn/attachments/20130825/9ac1a151/attachment.htm>


More information about the GSBN mailing list