Hey again all. This question came up on the NBNE list from Tristan
Roberts of BuildingGreen. Robert Riversong's response is included
below Tristan's post, but I thought someone over here might also have
more information on the purported Stramit lab test.
----- Forwarded message from tristan at buildinggreen.com -----
Hi,
Does anyone have insight into the R-value of compressed straw panels
such as Stramit (currently produced in Texas) or Agriboard (no longer
being produced)?
Stramit USA claims R-3.03/inch, and I have even seen press releases
claiming R-3.35. However, the company can't produce a lab test to
prove this to me, and there is history of R-value inflation in
compressed straw, as this old EBN article talks about:
http://www.buildinggreen.com/auth/article.cfm/1998/1/1/Agriboard-s-Inflated-R-value-Claims/
I supposed there might be less convective loops in a compressed straw
panel compared with a bale, but intuitively it's hard for me to
picture how compressed straw has higher R-value.
It's probably a longshot, but I wondered if anyone has any insight (or
maybe you know someone who might). Also, if you have any recent
experience with Stramit, I'd like to talk with you.
thanks!
Tristan
____________
Tristan Roberts
Editorial Director
BuildingGreen, Inc.
http://www.BuildingGreen.com
http://www.LEEDuser.com
(802) 257-7300 x121
tristan at buildinggreen.com
-----------end forwarded message -----------
Robert's reply:
Loose fibrous materials often increase in R-value per inch with
increased density - up to a point of diminishing returns - and I have
no reason to doubt that compressed straw would be more insulative than
straw bales.
Loose-fill fiberglass, for instance, is about R-2.5/inch, while
fiberglass batts, which used to be about R-3.14/inch for standard R-11
batts, were increased to R-13 (3.7/inch) in "high-density batts", and
semi-rigid fiberglass board as well as dense-pack Spider is about
R-4/inch.
Similarly, loose fill cellulose is about R-3.4/inch at 1.4 pcf
density, while dense-pack cellulose at 3+ pcf can be as much as
R-3.8/inch.
But the density range that Stramit specs of 15.6-40.5 pcf puts it at
about the same density range as solid wood, which is about
R-1.25/inch. So I also question their claim of R-3.35/inch.